No. A 4 wire 480V system is presumably a wye system, so the neutral to phase voltage is 277V. If the Bolt charger and the J1772 standard are rated for 277V, then you could charge using one phase conductor and one neutral. [I don't know about either of those questions.] Otherwise, you'd need a transformer.SeanNelson said:If you didn't want to go the L3 route then you'll be limited to 240V charging, which (and here I must warn you that I'm not an electrician) I imagine you could tap off one of the 480V phases.
gpsman said:What if I have convieniently placed 480 VAC power outlets? (4 wire 3 phase) Is this helpful for charging? How would I attach this to a Bolt EV?
The EVSE is just a very smart circuit breaker. It doesn't do any stepping down or up of voltage. It just advertises to the car how amperage it can supply and waits for the car to signal it to start suppling electricity. Unless the car's internal charger is capable of accepting 277VAC, you do not want to hookup that much voltage to it because of the risk of frying the charger and/or starting a fire in the car. Even Teslas aren't capable of 277VAC. They max out at 265.gpsman said:I was reading about the wye connection and the 277 VAC one leg to ground.
I am mostly wondering is 277 V is "close enough" for a 240 VAC EVSE.
I'm thinking about how many consumer electronics (low power - shavers, etc - for international travel) work on multiple voltages.
Ah, NEMA L16 doesn't provide a neutral, it's 3 phase conductors plus ground. So the only voltage available is 480V, there's no chance of hooking up an EVSE directly. You'd need to add a transformer to drop the voltage from 480V to 240V to use that receptacle.gpsman said:30 Amps - Voltage 480VAC - Number of Poles 3 - Number of Wires 4 - L16-30R NEMA Configuration - Phase 3 - HP 10.0
wwhitney said:Ah, NEMA L16 doesn't provide a neutral, it's 3 phase conductors plus ground. So the only voltage available is 480V, there's no chance of hooking up an EVSE directly. You'd need to add a transformer to drop the voltage from 480V to 240V to use that receptacle.gpsman said:30 Amps - Voltage 480VAC - Number of Poles 3 - Number of Wires 4 - L16-30R NEMA Configuration - Phase 3 - HP 10.0
Cheers, Wayne