How do I connect an AV Turbo Cord L2 EVSE to the 14-50r, 240 VAC at Frazier Park? MichaelLAX - you posted what you did but I would like the details so I know what I need to purchase.
Thanks
Thanks
Thanks for the useful information. I just checked Clipper Creek and they have L2 EVSEs that will connect to a 14-50 socket or a 14-30 socket depending which option you choose. Frazier Park has a 240V 14-30 outlet. I was trying to figure out how to add charge at Frazier Park if I wanted to make a "stress-free" run from the Central Valley of California to Los Angeles in my Spark EV. It would be an easy drive in a Bolt EV.SparkE said:You need a cable ('extension cord', 'pigtail', 'Adapter' - whatever you want to call it) that has a NEMA 14-50P plug on one side (that you plug into the wall), and a NEMA 6-20R receptacle (i.e., 'socket') on the other end (into which you will plug your TurboCord Dual 240V/120V or TurboCord 240V, which have NEMA6-20 plugs).
Since both NEMA 14 and NEMA 6 have two 'hot' wires and one ground wire AND you are plugging a device that won't pull over 20 amps into a circuit that should be rated for 50A (40A continuous), it is a completely safe conversion (so long as the gauge of the wire in the cord is sufficiently robust). Note that NEMA 14 also has a 'neutral', but that will just be ignored (not connected) to the NEMA6 side.
You can buy one here : https://evse-adapters.myshopify.com/collections/other-adapters/products/nema-6-20r-to-14-30-14-50-14-60-universal-adapter I am NOT recommending this particular item. I don't know if it is good quality or not. I am providing the link simply so that you can see an example of what I am talking about. I am fairly certain that there are other manufacturers. An advantage of this one is that they claim that it can be inserted into 14-30/14-50/14-60 receptacles (because the un-connected 'neutral' prong is the one that changes form on each of the different-rated receptacles, and the NEMA6 plug doesn't use it) - AND since the 6-20 will pull fewer than 30/50/60 amps, it should be safe.
In case the URL gets munged, it looks like ('exploded' version) :
http evse-adapters.myshopify.com collections/other-adapters/products/nema-6-20r-to-14-30-14-50-14-60-universal-adapter
djbiggs59 said:My wife has a 240-volt NEMA 240 VAC 14-50 outlet in our garage to charge her Tesla S vehicle. I would like to use this outlet to charge a 2017 Chevrolet Bolt using the same 14-50 outlet, and I know that I need an adapter to connect the charger from the Bolt to the 14-50 outlet. Grateful for confirmation of the types of adapters which can be used.
djbiggs59 said:My wife has a 240-volt NEMA 240 VAC 14-50 outlet in our garage to charge her Tesla S vehicle. I would like to use this outlet to charge a 2017 Chevrolet Bolt using the same 14-50 outlet, and I know that I need an adapter to connect the charger from the Bolt to the 14-50 outlet. Grateful for confirmation of the types of adapters which can be used.
EldRick said:Or just install a second outlet on the circuit and set the cars so they do not both charge at the same time.
djbiggs59 said:My wife has a 240-volt NEMA 240 VAC 14-50 outlet in our garage to charge her Tesla S vehicle. I would like to use this outlet to charge a 2017 Chevrolet Bolt using the same 14-50 outlet, and I know that I need an adapter to connect the charger from the Bolt to the 14-50 outlet. Grateful for confirmation of the types of adapters which can be used.
sgt1372 said:djbiggs59 said:My wife has a 240-volt NEMA 240 VAC 14-50 outlet in our garage to charge her Tesla S vehicle. I would like to use this outlet to charge a 2017 Chevrolet Bolt using the same 14-50 outlet, and I know that I need an adapter to connect the charger from the Bolt to the 14-50 outlet. Grateful for confirmation of the types of adapters which can be used.
I've got a 240v/50A circuit w/a NEMA 14-50 outlet installed in my garage for the L1 lipper Creek HCS-40P that I also installed to charge my Bolt.
However, I don't think you can "safely" connect the the L1 charger that came w/your Bolt to the NEMA 14-50 outlet because it is set up for 120V. Someone said that the transformer connected to the Bolt L1 charger is actually dual phased and can run 240 or 120 but, if it was designed that way, why wasn't it offered as a dual charger in the 1st place? So, unless you're a competent electrician and know what you're doing, I wouldn't attempt it.
Just plug the L1 charger into a 120v outlet as designed and set your Bolt for 12A charging or get a L2 Clipper Creek (or other compatible) charger to plug into the NEMA 14-50 outlet instead.
cosmacelf said:EldRick said:Or just install a second outlet on the circuit and set the cars so they do not both charge at the same time.
That would be against code since the likelihood of a screw up is high, resulting in best case a tripped breaker, worse case, an electrical fire.
I believe that @cosmacelf is referring to 240V circuits/outlets, not 120V outlets.SparkE said:cosmacelf said:EldRick said:Or just install a second outlet on the circuit and set the cars so they do not both charge at the same time.
That would be against code since the likelihood of a screw up is high, resulting in best case a tripped breaker, worse case, an electrical fire.
Are you sure it would be against code? All of the 120V sockets in my house are wired to 15 or 20 Amp breakers, and there are multiple sockets wired into each breaker (at least 3 - up to 6 or more ins a couple of cases). That seems to be the same thing to me.
devbolt said:You can safely connect the 120V EVSE that comes with the Bolt to a 240V recepetcle if you have the right adapters:
http://gm-volt.com/forum/showthread.php?218442-2016-Volt-120v-EVSE-is-L1-L2-Conversion-Capable
We aims to please!gbobman said:devbolt said:You can safely connect the 120V EVSE that comes with the Bolt to a 240V recepetcle if you have the right adapters:
http://gm-volt.com/forum/showthread.php?218442-2016-Volt-120v-EVSE-is-L1-L2-Conversion-Capable
That's where I saw it. Thank you, I've been looking for that for a while now.
devbolt said:I believe that @cosmacelf is referring to 240V circuits/outlets, not 120V outlets.SparkE said:cosmacelf said:That would be against code since the likelihood of a screw up is high, resulting in best case a tripped breaker, worse case, an electrical fire.
Are you sure it would be against code? All of the 120V sockets in my house are wired to 15 or 20 Amp breakers, and there are multiple sockets wired into each breaker (at least 3 - up to 6 or more ins a couple of cases). That seems to be the same thing to me.
SparkE said:devbolt said:I believe that @cosmacelf is referring to 240V circuits/outlets, not 120V outlets.SparkE said:Are you sure it would be against code? All of the 120V sockets in my house are wired to 15 or 20 Amp breakers, and there are multiple sockets wired into each breaker (at least 3 - up to 6 or more ins a couple of cases). That seems to be the same thing to me.
Yes, but the principle is the same. A bunch of sockets are strung off the same breaker. The breaker matches the max rating for any ONE of the sockets. In the case I mentioned, the same wires (yes, using 'hot' + 'neutral', instead of 'hot' + 'hot') are used to pull the current off the same breaker, off the same busbar. That is SOP in homes and has been for a long time and is definitely 'in code'. Do local codes specify that 240V breakers must have exactly one socket attached to it, and no more?
240V circuits can have multiple receptacles, however the circuit must be sized for the load to be served. If you have one EVSE (or welder) that you want to be able to move around and use in different locations, you can put multiple receptacles on one circuit for that purposes. However if you have two EVSEs on the same circuit, you will need to size the circuit to the maximum load that could be drawn. From the (2011) NEC article on EVSEs:SparkE said:Do local codes specify that 240V breakers must have exactly one socket attached to it, and no more?
625.21 said:Overcurrent protection for feeders and branch circuits supplying electric vehicle supply equipment shall be sized for continuous duty and shall have a rating of not less than 125 percent of the maximum load of the electric vehicle supply equipment.