wwhitney said:240V circuits can have multiple receptacles, however the circuit must be sized for the load to be served. If you have one EVSE (or welder) that you want to be able to move around and use in different locations, you can put multiple receptacles on one circuit for that purposes. However if you have two EVSEs on the same circuit, you will need to size the circuit to the maximum load that could be drawn. From the (2011) NEC article on EVSEs:SparkE said:Do local codes specify that 240V breakers must have exactly one socket attached to it, and no more?
625.21 said:Overcurrent protection for feeders and branch circuits supplying electric vehicle supply equipment shall be sized for continuous duty and shall have a rating of not less than 125 percent of the maximum load of the electric vehicle supply equipment.
I doubt any jurisdiction is going to interpret "maximum load" to be reduced in the case of "human interlocking." On the other hand, two EVSEs that communicate with each other to enforce a cap on their joint load would reduce the "maximum load".
Cheers, Wayne
ChargePoint has dual-headed EVSEs that share a single circuit. The EVSE provides full power if only one car is charging, otherwise it splits the available power equally between the two cars. If one car finishes, the other gets full power if it needs it.
I'm no electrician, but the paranoid side of me says that multiple sockets on a 240V circuit is not the smartest thing to do because you know a homeowner will do something stupid and plug-in two high-draw devices at the same time not realizing they are on a single circuit. Or forget that it's a shared circuit. The smart play seems to be just to install two circuits if there is room in the panel.